Cooling tower
Overview
 
Cooling towers are heat removal devices used to transfer process waste heat to the atmosphere
Atmosphere
An atmosphere is a layer of gases that may surround a material body of sufficient mass, and that is held in place by the gravity of the body. An atmosphere may be retained for a longer duration, if the gravity is high and the atmosphere's temperature is low...

. Cooling towers may either use the evaporation
Evaporation
Evaporation is a type of vaporization of a liquid that occurs only on the surface of a liquid. The other type of vaporization is boiling, which, instead, occurs on the entire mass of the liquid....

 of water to remove process heat and cool the working fluid to near the wet-bulb air temperature
Wet-bulb temperature
The wet-bulb temperature is a type of temperature measurement that reflects the physical properties of a system with a mixture of a gas and a vapor, usually air and water vapor. Wet bulb temperature is the lowest temperature that can be reached by the evaporation of water only. It is the...

 or in the case of closed circuit dry cooling towers rely solely on air to cool the working fluid to near the dry-bulb air temperature
Dry-bulb temperature
The dry-bulb temperature is the temperature of air measured by a thermometer freely exposed to the air but shielded from radiation and moisture. Dry bulb temperature is the temperature that is usually thought of as air temperature, and it is the true thermodynamic temperature. It is the...

. Common applications include cooling the circulating water used in oil refineries, chemical plant
Chemical plant
A chemical plant is an industrial process plant that manufactures chemicals, usually on a large scale. The general objective of a chemical plant is to create new material wealth via the chemical or biological transformation and or separation of materials. Chemical plants use special equipment,...

s, power station
Power station
A power station is an industrial facility for the generation of electric energy....

s and building cooling.
Encyclopedia
Cooling towers are heat removal devices used to transfer process waste heat to the atmosphere
Atmosphere
An atmosphere is a layer of gases that may surround a material body of sufficient mass, and that is held in place by the gravity of the body. An atmosphere may be retained for a longer duration, if the gravity is high and the atmosphere's temperature is low...

. Cooling towers may either use the evaporation
Evaporation
Evaporation is a type of vaporization of a liquid that occurs only on the surface of a liquid. The other type of vaporization is boiling, which, instead, occurs on the entire mass of the liquid....

 of water to remove process heat and cool the working fluid to near the wet-bulb air temperature
Wet-bulb temperature
The wet-bulb temperature is a type of temperature measurement that reflects the physical properties of a system with a mixture of a gas and a vapor, usually air and water vapor. Wet bulb temperature is the lowest temperature that can be reached by the evaporation of water only. It is the...

 or in the case of closed circuit dry cooling towers rely solely on air to cool the working fluid to near the dry-bulb air temperature
Dry-bulb temperature
The dry-bulb temperature is the temperature of air measured by a thermometer freely exposed to the air but shielded from radiation and moisture. Dry bulb temperature is the temperature that is usually thought of as air temperature, and it is the true thermodynamic temperature. It is the...

. Common applications include cooling the circulating water used in oil refineries, chemical plant
Chemical plant
A chemical plant is an industrial process plant that manufactures chemicals, usually on a large scale. The general objective of a chemical plant is to create new material wealth via the chemical or biological transformation and or separation of materials. Chemical plants use special equipment,...

s, power station
Power station
A power station is an industrial facility for the generation of electric energy....

s and building cooling. The towers vary in size from small roof-top units to very large hyperboloid structure
Hyperboloid structure
Hyperboloid structures are architectural structures designed with hyperboloid geometry. Often these are tall structures such as towers where the hyperboloid geometry's structural strength is used to support an object high off the ground, but hyperboloid geometry is also often used for decorative...

s (as in Image 1) that can be up to 200 metres tall and 100 metres in diameter, or rectangular structures (as in Image 2) that can be over 40 metres tall and 80 metres long. Smaller towers are normally factory-built, while larger ones are constructed on site. They are often associated with nuclear power plants in popular culture, although cooling towers are constructed on many types of buildings.

A hyperboloid
Hyperboloid structure
Hyperboloid structures are architectural structures designed with hyperboloid geometry. Often these are tall structures such as towers where the hyperboloid geometry's structural strength is used to support an object high off the ground, but hyperboloid geometry is also often used for decorative...

 cooling tower was patented by Frederik van Iterson and Gerard Kuypers in 1918. The first hyperboloid cooling towers were built in the last 1920s in Liverpool, England to cool water used at a electrical power station that used coal.

HVAC

An HVAC (heating, ventilating, and air conditioning) cooling tower is a subcategory rejecting heat from a chiller
Chiller
A chiller is a machine that removes heat from a liquid via a vapor-compression or absorption refrigeration cycle. This liquid can then be circulated through a heat exchanger to cool air or equipment as required.-Use in air conditioning:...

. Water-cooled chillers are normally more energy efficient than air-cooled chillers due to heat rejection to tower water at or near wet-bulb temperatures. Air-cooled chillers must reject heat at the dry-bulb temperature, and thus have a lower average reverse-Carnot cycle effectiveness. Large office buildings, hospitals, and schools typically use one or more cooling towers as part of their air conditioning systems. Generally, industrial cooling towers are much larger than HVAC towers.

HVAC use of a cooling tower pairs the cooling tower with a water-cooled chiller or water-cooled condenser. A ton of air-conditioning is the removal of 12,000 Btu/hour (3500 W). The equivalent ton on the cooling tower side actually rejects about 15,000 Btu/hour (4400 W) due to the heat-equivalent of the energy needed to drive the chiller's compressor. This equivalent ton is defined as the heat rejection in cooling 3 U.S. gallons/minute (1,500 pound/hour) of water 10 °F (6 °C), which amounts to 15,000 Btu/hour, or a chiller coefficient of performance (COP) of 4.0. This COP is equivalent to an energy efficiency ratio (EER) of 14.

Cooling towers are also used in HVAC systems that have multiple water source heat pumps that share a common piping water loop. In this type of system, the water circulating inside the water loop removes heat from the condenser of the heat pumps whenever the heat pumps are working in the cooling mode, then the cooling tower is used to remove heat from the water loop and reject it to the atmosphere
Atmosphere
An atmosphere is a layer of gases that may surround a material body of sufficient mass, and that is held in place by the gravity of the body. An atmosphere may be retained for a longer duration, if the gravity is high and the atmosphere's temperature is low...

. When the heat pumps are working in heating mode, the condensers draw heat out of the loop water and reject it into the space to be heated.

Industrial cooling towers

Industrial cooling towers can be used to remove heat from various sources such as machinery or heated process material. The primary use of large, industrial cooling towers is to remove the heat absorbed in the circulating cooling water systems used in power plants, petroleum refineries
Oil refinery
An oil refinery or petroleum refinery is an industrial process plant where crude oil is processed and refined into more useful petroleum products, such as gasoline, diesel fuel, asphalt base, heating oil, kerosene, and liquefied petroleum gas...

, petrochemical
Petrochemical
Petrochemicals are chemical products derived from petroleum. Some chemical compounds made from petroleum are also obtained from other fossil fuels, such as coal or natural gas, or renewable sources such as corn or sugar cane....

 plants, natural gas
Natural gas
Natural gas is a naturally occurring gas mixture consisting primarily of methane, typically with 0–20% higher hydrocarbons . It is found associated with other hydrocarbon fuel, in coal beds, as methane clathrates, and is an important fuel source and a major feedstock for fertilizers.Most natural...

 processing plants, food processing plants, semi-conductor plants, and for other industrial facilities such as in condensers of distillation columns, for cooling liquid in crystallization, etc. The circulation rate of cooling water in a typical 700 MW coal-fired power plant with a cooling tower amounts to about 71,600 cubic metres an hour (315,000 U.S. gallons per minute) and the circulating water requires a supply water make-up rate of perhaps 5 percent (i.e., 3,600 cubic metres an hour).

If that same plant had no cooling tower and used once-through cooling water, it would require about 100,000 cubic metres an hour and that amount of water would have to be continuously returned to the ocean, lake or river from which it was obtained and continuously re-supplied to the plant. Furthermore, discharging large amounts of hot water may raise the temperature of the receiving river or lake to an unacceptable level for the local ecosystem. Elevated water temperatures can kill fish
Fish
Fish are a paraphyletic group of organisms that consist of all gill-bearing aquatic vertebrate animals that lack limbs with digits. Included in this definition are the living hagfish, lampreys, and cartilaginous and bony fish, as well as various extinct related groups...

 and other aquatic organisms (see thermal pollution
Thermal pollution
Thermal pollution is the degradation of water quality by any process that changes ambient water temperature.A common cause of thermal pollution is the use of water as a coolant by power plants and industrial manufacturers...

). A cooling tower serves to dissipate the heat into the atmosphere instead and wind and air diffusion spreads the heat over a much larger area than hot water can distribute heat in a body of water.
Some coal-fired and nuclear power plant
Nuclear power plant
A nuclear power plant is a thermal power station in which the heat source is one or more nuclear reactors. As in a conventional thermal power station the heat is used to generate steam which drives a steam turbine connected to a generator which produces electricity.Nuclear power plants are usually...

s located in coastal areas do make use of once-through ocean water. But even there, the offshore discharge water outlet requires very careful design to avoid environmental problems.

Petroleum refineries also have very large cooling tower systems. A typical large refinery processing 40,000 metric tonnes of crude oil per day (300000 barrels (47,696,188.5 l) per day) circulates about 80,000 cubic metres of water per hour through its cooling tower system.

The world's tallest cooling tower is the 200 metres tall cooling tower of Niederaussem Power Station
Niederaussem Power Station
Niederaussem Power Station is a lignite-fired power station in the Bergheim Niederaussem/Rhein Erft circle, owned by RWE. It consists of nine units, which were built between 1963 and 2003. It has a total output capacity of 3,864 MW and a net capacity of 3,627 MW...

.

Package Type

This type of cooling towers are preassembled and can be simply transported on trucks as they are compact machines. The capacity of package type towers is limited and for that reason, they are usually preferred by facilities with low heat rejection requirements such as food processing plants, textile plants, buildings like hospitals, hotels, malls, chemical processing plants, automotive factories etc.

Due to intensive use in domestic areas, sound level control is a relatively more important issue for package type cooling towers.

Field Erected Type

Such facilities as power plants, steel processing plants, petroleum refineries, petrochemical plants prefer field erected type cooling towers due to their large requirements of heat rejection. These towers are a lot larger in size compared to the package type cooling towers. A typical field erected cooling tower has pultruded FRP structure, FRP cladding, a mechanical unit for air draft, drift eliminator and fill.

Heat transfer methods

With respect to the heat transfer
Heat transfer
Heat transfer is a discipline of thermal engineering that concerns the exchange of thermal energy from one physical system to another. Heat transfer is classified into various mechanisms, such as heat conduction, convection, thermal radiation, and phase-change transfer...

 mechanism employed, the main types are:
  • Wet cooling towers or simply open circuit cooling towers operate on the principle of evaporation. The working fluid and the evaporated fluid (usually water) are one and the same.
  • Dry cooling towers operate by heat transfer
    Heat transfer
    Heat transfer is a discipline of thermal engineering that concerns the exchange of thermal energy from one physical system to another. Heat transfer is classified into various mechanisms, such as heat conduction, convection, thermal radiation, and phase-change transfer...

     through a surface that separates the working fluid from ambient air, such as in a tube to air heat exchanger
    Heat exchanger
    A heat exchanger is a piece of equipment built for efficient heat transfer from one medium to another. The media may be separated by a solid wall, so that they never mix, or they may be in direct contact...

    , utilizing convective heat transfer. They do not use evaporation.
  • Fluid coolers or closed circuit cooling towers are hybrids that pass the working fluid through a tube bundle, upon which clean water is sprayed and a fan-induced draft applied. The resulting heat transfer performance is much closer to that of a wet cooling tower, with the advantage provided by a dry cooler of protecting the working fluid from environmental exposure and contamination.


In a wet cooling tower (or open circuit cooling tower), the warm water can be cooled to a temperature lower than the ambient air dry-bulb temperature, if the air is relatively dry (see dew point
Dew point
The dew point is the temperature to which a given parcel of humid air must be cooled, at constant barometric pressure, for water vapor to condense into liquid water. The condensed water is called dew when it forms on a solid surface. The dew point is a saturation temperature.The dew point is...

and psychrometrics
Psychrometrics
Psychrometrics or psychrometry or Hygrometry are terms used to describe the field of engineering concerned with the determination of physical and thermodynamic properties of gas-vapor mixtures...

). As ambient air is drawn past a flow of water, a small portion of the water evaporate, the energy required by that portion of the water to evaporate is taken from the remaining mass of water reducing his temperature (approximately by 970 BTU for each pound of evaporated water). Evaporation results in saturated air conditions, lowering the temperature of the water process by the tower to a value close to wet bulb air temperature, which is lower than the ambient dry bulb air temperature, the difference determined by the humidity of the ambient air.

To achieve better performance (more cooling), a medium called fill is used to increase the surface area and the time of contact between the air and water flows. Splash fill consists of material placed to interrupt the water flow causing splashing. Film fill is composed of thin sheets of material (usually PVC) upon which the water flows. Both methods create increased surface area and time of contact between the fluid (water) and the gas (air).

Air flow generation methods


With respect to drawing air through the tower, there are three types of cooling towers:
  • Natural draft
    Stack effect
    Stack effect is the movement of air into and out of buildings, chimneys, flue gas stacks, or other containers, and is driven by buoyancy. Buoyancy occurs due to a difference in indoor-to-outdoor air density resulting from temperature and moisture differences. The result is either a positive or...

    , which utilizes buoyancy via a tall chimney. Warm, moist air naturally rises due to the density differential to the dry, cooler outside air. Warm moist air is less dense than drier air at the same pressure. This moist air buoyancy produces a current of air through the tower.
  • Mechanical draft, which uses power driven fan motors to force or draw air through the tower.
    • Induced draft: A mechanical draft tower with a fan at the discharge which pulls air through tower. The fan induces hot moist air out the discharge. This produces low entering and high exiting air velocities, reducing the possibility of recirculation in which discharged air flows back into the air intake. This fan/fin arrangement is also known as draw-through. (see Image 3)
    • Forced draft: A mechanical draft tower with a blower type fan at the intake. The fan forces air into the tower, creating high entering and low exiting air velocities. The low exiting velocity is much more susceptible to recirculation. With the fan on the air intake, the fan is more susceptible to complications due to freezing conditions. Another disadvantage is that a forced draft design typically requires more motor horsepower than an equivalent induced draft design. The forced draft benefit is its ability to work with high static pressure. They can be installed in more confined spaces and even in some indoor situations. This fan/fill geometry is also known as blow-through. (see Image 4)
  • Fan assisted natural draft. A hybrid type that appears like a natural draft though airflow is assisted by a fan.


Hyperboloid (sometimes incorrectly known as hyperbolic
Hyperbolic
Hyperbolic refers to something related to or in shape of hyperbola , or to something employing the literary device of hyperbole .The following topics are based on the hyperbola etymology:...

) cooling towers (Image 1) have become the design standard for all natural-draft cooling towers because of their structural strength and minimum usage of material. The hyperboloid shape also aids in accelerating the upward convective
Convection
Convection is the movement of molecules within fluids and rheids. It cannot take place in solids, since neither bulk current flows nor significant diffusion can take place in solids....

 air flow, improving cooling efficiency. They are popularly associated with nuclear power plant
Nuclear power plant
A nuclear power plant is a thermal power station in which the heat source is one or more nuclear reactors. As in a conventional thermal power station the heat is used to generate steam which drives a steam turbine connected to a generator which produces electricity.Nuclear power plants are usually...

s. However, this association is misleading, as the same kind of cooling towers are often used at large coal-fired power plants as well. Similarly, not all nuclear power plants have cooling towers, instead cooling their heat exchangers with lake, river or ocean water.

Crossflow

Crossflow is a design in which the air flow is directed perpendicular to the water flow (see diagram below). Air flow enters one or more vertical faces of the cooling tower to meet the fill material. Water flows (perpendicular to the air) through the fill by gravity. The air continues through the fill and thus past the water flow into an open plenum area. A distribution or hot water basin consisting of a deep pan with holes or nozzles in the bottom is utilized in a crossflow tower. Gravity distributes the water through the nozzles uniformly across the fill material.


Counterflow

In a counterflow design the air flow is directly opposite to the water flow (see diagram below). Air flow first enters an
open area beneath the fill media and is then drawn up vertically. The water is sprayed through pressurized nozzles and flows downward through the fill, opposite to the air flow.



Common to both designs:
  • The interaction of the air and water flow allow a partial equalization and evaporation of water.
  • The air, now saturated with water vapor, is discharged from the cooling tower.
  • A collection or cold water basin is used to contain the water after its interaction with the air flow.


Both crossflow and counterflow designs can be used in natural draft and mechanical draft cooling towers.

Cooling tower as a flue gas stack

At some modern power stations, equipped with flue gas purification
Flue gas desulfurization
Sulfur dioxide is one of the elements forming acid rain. Tall flue-gas stacks disperse emissions by diluting the pollutants in ambient air and transporting them to other regions....

 like the Power Station Staudinger Grosskrotzenburg and the Power Station Rostock, the cooling tower is also used as a flue gas stack
Flue gas stack
A flue-gas stack is a type of chimney, a vertical pipe, channel or similar structure through which combustion product gases called flue gases are exhausted to the outside air. Flue gases are produced when coal, oil, natural gas, wood or any other fuel is combusted in an industrial furnace, a power...

 (industrial chimney). At plants without flue gas purification, problems with corrosion may occur.
123

Wet cooling tower material balance

Quantitatively, the material balance around a wet, evaporative cooling tower system is governed by the operational variables of makeup flow rate, evaporation
Evaporation
Evaporation is a type of vaporization of a liquid that occurs only on the surface of a liquid. The other type of vaporization is boiling, which, instead, occurs on the entire mass of the liquid....

 and windage losses, draw-off rate, and the concentration cycles:


M = Make-up water in m³/h
C = Circulating water in m³/h
D = Draw-off water in m³/h
E = Evaporated water in m³/h
W = Windage loss of water in m³/h
X = Concentration in ppmw (of any completely soluble salts … usually chlorides)
XM = Concentration of chloride
Chloride
The chloride ion is formed when the element chlorine, a halogen, picks up one electron to form an anion Cl−. The salts of hydrochloric acid HCl contain chloride ions and can also be called chlorides. The chloride ion, and its salts such as sodium chloride, are very soluble in water...

s in make-up water (M), in ppmw
XC = Concentration of chlorides in circulating water (C), in ppmw
Cycles = Cycles of concentration = XC / XM (dimensionless)
ppmw = parts per million by weight


In the above sketch, water pumped from the tower basin is the cooling water routed through the process coolers and condensers
Condenser (steam turbine)
A surface condenser is a commonly used term for a water-cooled shell and tube heat exchanger installed on the exhaust steam from a steam turbine in thermal power stations. These condensers are heat exchangers which convert steam from its gaseous to its liquid state at a pressure below atmospheric...

 in an industrial facility. The cool water absorbs heat from the hot process streams which need to be cooled or condensed, and the absorbed heat warms the circulating water (C). The warm water returns to the top of the cooling tower and trickles downward over the fill material inside the tower. As it trickles down, it contacts ambient air rising up through the tower either by natural draft or by forced draft using large fans in the tower. That contact causes a small amount of the water to be lost as windage (W) and some of the water (E) to evaporate
Evaporation
Evaporation is a type of vaporization of a liquid that occurs only on the surface of a liquid. The other type of vaporization is boiling, which, instead, occurs on the entire mass of the liquid....

. The heat required to evaporate the water is derived from the water itself, which cools the water back to the original basin water temperature and the water is then ready to recirculate. The evaporated water leaves its dissolved salt
Salt
In chemistry, salts are ionic compounds that result from the neutralization reaction of an acid and a base. They are composed of cations and anions so that the product is electrically neutral...

s behind in the bulk of the water which has not been evaporated, thus raising the salt concentration in the circulating cooling water. To prevent the salt concentration of the water from becoming too high, a portion of the water is drawn off (D) for disposal. Fresh water makeup (M) is supplied to the tower basin to compensate for the loss of evaporated water, the windage loss water and the draw-off water.

A water balance around the entire system is:
M = E + D + W


Since the evaporated water (E) has no salts, a chloride balance around the system is:
M (XM) = D (XC) + W (XC) = XC (D + W)


and, therefore:
XC / XM = Cycles of concentration = M ÷ (D + W) = M ÷ (M – E) = 1 + [E ÷ (D + W)]


From a simplified heat balance around the cooling tower:
E = C · ΔT · cp ÷ HV

where:  
HV = latent heat of vaporization of water = ca. 2260 kJ / kg
ΔT = water temperature difference from tower top to tower bottom, in °C
cp = specific heat of water = ca. 4.184 kJ / (kg°C)


Windage (or drift) losses (W) from large-scale industrial cooling towers, in the absence of manufacturer's data, may be assumed to be:
W = 0.3 to 1.0 percent of C for a natural draft cooling tower without windage drift eliminators
W = 0.1 to 0.3 percent of C for an induced draft cooling tower without windage drift eliminators
W = about 0.005 percent of C (or less) if the cooling tower has windage drift eliminators


Cycles of concentration represents the accumulation of dissolved minerals in the recirculating cooling water. Draw-off (or blowdown) is used principally to control the buildup of these minerals.

The chemistry of the makeup water including the amount of dissolved minerals can vary widely. Makeup waters low in dissolved minerals such as those from surface water supplies (lakes, rivers etc.) tend to be aggressive to metals (corrosive). Makeup waters from ground water supplies (wells) are usually higher in minerals and tend to be scaling
Limescale
Limescale is the hard, off-white, chalky deposit found in kettles, hot-water boilers and the inside of inadequately maintained hot-water central heating systems...

 (deposit minerals). Increasing the amount of minerals present in the water by cycling can make water less aggressive to piping however excessive levels of minerals can cause scaling problems.

As the cycles of concentration increase the water may not be able to hold the minerals in solution. When the solubility
Solubility
Solubility is the property of a solid, liquid, or gaseous chemical substance called solute to dissolve in a solid, liquid, or gaseous solvent to form a homogeneous solution of the solute in the solvent. The solubility of a substance fundamentally depends on the used solvent as well as on...

 of these minerals have been exceeded they can precipitate out as mineral solids and cause fouling and heat exchange problems in the cooling tower or the heat exchangers. The temperatures of the recirculating water, piping and heat exchange surfaces determine if and where minerals will precipitate from the recirculating water. Often a professional water treatment consultant will evaluate the makeup water and the operating conditions of the cooling tower and recommend an appropriate range for the cycles of concentration. The use of water treatment chemicals, pretreatment such as water softening
Water softening
Water softening is the reduction of the concentration of calcium, magnesium, and certain other metal cations in hard water. These "hardness ions" can cause a variety of undesired effects including interfering with the action of soaps, the build up of limescale, which can foul plumbing, and...

, pH
PH
In chemistry, pH is a measure of the acidity or basicity of an aqueous solution. Pure water is said to be neutral, with a pH close to 7.0 at . Solutions with a pH less than 7 are said to be acidic and solutions with a pH greater than 7 are basic or alkaline...

 adjustment, and other techniques can affect the acceptable range of cycles of concentration.

Concentration cycles in the majority of cooling towers usually range from 3 to 7. In the United States the majority of water supplies are well waters and have significant levels of dissolved solids. On the other hand one of the largest water supplies, New York City, has a surface supply quite low in minerals and cooling towers in that city are often allowed to concentrate to 7 or more cycles of concentration.

Besides treating the circulating cooling water in large industrial cooling tower systems to minimize scaling
Scaling
Scaling may refer to:* Scaling , a linear transformation that enlarges or diminishes objects* Reduced scales of semiconductor device fabrication processes...

 and fouling
Fouling
Fouling refers to the accumulation of unwanted material on solid surfaces, most often in an aquatic environment. The fouling material can consist of either living organisms or a non-living substance...

, the water should be filtered
Filter (water)
A water filter removes impurities from water by means of a fine physical barrier, a chemical process or a biological process. Filters cleanse water to various extents for irrigation, drinking water, aquariums, and swimming pools.-Methods of filtration:...

 and also be dosed with biocide
Biocide
A biocide is a chemical substance or microorganism which can deter, render harmless, or exert a controlling effect on any harmful organism by chemical or biological means. Biocides are commonly used in medicine, agriculture, forestry, and industry...

s and algaecide
Algaecide
An algaecide or algicide is a substance used for killing and preventing the growth of algae.-Natural algicides:Barley straw, in England, is placed in mesh bags and floated in fish ponds or water gardens to help reduce algal growth without harming pond plants and animals...

s to prevent growths that could interfere with the continuous flow of the water. For closed loop evaporative towers, corrosion inhibitors may be used, but caution should be taken to meet local environmental regulations as some inhibitors use chromate
Chromate
Chromate salts contain the chromate anion, CrO42−. Dichromate salts contain the dichromate anion, Cr2O72−. They are oxyanions of chromium in the oxidation state +6. They are moderately strong oxidizing agents.- Chemical properties :...

s.

Ambient conditions dictate the efficiency of any given tower due to the amount of water vapor the air is able to absorb and hold, as can be determined on a psychrometric chart.

Cooling towers and Legionnaires' disease


Another very important reason for using biocides in cooling towers is to prevent the growth of Legionella
Legionella
Legionella is a pathogenic Gram negative bacterium, including species that cause legionellosis or Legionnaires' disease, most notably L. pneumophila. It may be readily visualized with a silver stain....

, including species that cause legionellosis
Legionellosis
Legionellosis is a potentially fatal infectious disease caused by gram negative, aerobic bacteria belonging to the genus Legionella. Over 90% of legionellosis cases are caused by Legionella pneumophila, a ubiquitous aquatic organism that thrives in temperatures between , with an optimum temperature...

 or Legionnaires' disease, most notably L. pneumophila, or Mycobacterium avium. The various Legionella species are the cause of Legionnaires' disease in humans and transmission is via exposure to aerosols—the inhalation of mist droplets containing the bacteria. Common sources of Legionella include cooling towers used in open recirculating evaporative cooling water systems, domestic hot water systems, fountains, and similar disseminators that tap into a public water supply. Natural sources include freshwater ponds and creeks.

French researchers found that Legionella bacteria travelled up to 6 kilometres through the air from a large contaminated cooling tower at a petrochemical plant in Pas-de-Calais, France. That outbreak killed 21 of the 86 people who had a laboratory-confirmed infection.

Drift (or windage) is the term for water droplets of the process flow allowed to escape in the cooling tower discharge. Drift eliminators are used in order to hold drift rates typically to 0.001%-0.005% of the circulating flow rate. A typical drift eliminator provides multiple directional changes of airflow while preventing the escape of water droplets. A well-designed and well-fitted drift eliminator can greatly reduce water loss and potential for Legionella or other chemical exposure.

Many governmental agencies, cooling tower manufacturers and industrial trade organizations have developed design and maintenance guidelines for preventing or controlling the growth of Legionella in cooling towers. Below is a list of sources for such guidelines:
- Procedure for Cleaning Cooling Towers and Related Equipment (pages 239 and 240 of 249) - Best Practices for Control of Legionella, July, 2006 - Legionella 2003 - Cooling Water Management Program Guidelines For Wet and Hybrid Cooling Towers at Power Plants - Cooling Towers Maintenance Procedures - ASHRAE Guideline 12-2000 - Minimizing the Risk of Legionellosis - Cooling Tower Inspection Tips {especially page 3 of 7} - Legionella Control - Chemical Water Treatment Recommendations For Reduction of Risks Associated with Legionella in Open Recirculating Cooling Water Systems

Cooling tower fog

Under certain ambient conditions, plumes of water vapor (fog) can be seen rising out of the discharge from a cooling tower, and can be mistaken as smoke from a fire. If the outdoor air is at or near saturation, and the tower adds more water to the air, saturated air with liquid water droplets can be discharged—which is seen as fog. This phenomenon typically occurs on cool, humid days, but is rare in many climates.

This phenomenon can be prevented by decreasing the relative humidity of the saturated discharge air. For that purpose, in hybrid towers, saturated discharge air is mixed with heated low relative humidity air. Some air enters the tower above drift eliminator level, passing through heat exchangers. The relative humidity of the dry air is even more decreased instantly as being heated while entering the tower. The discharged mixture has a relatively lower relative humidity and the fog is invisible.

Cooling tower operation in freezing weather

Cooling towers with malfunctions can freeze during very cold weather. Typically, freezing starts at the corners of a cooling tower with a reduced or absent heat load. Increased freezing conditions can create growing volumes of ice, resulting in increased structural loads. During the winter, some sites continuously operate cooling towers with 40 °F (4.4 °C) water leaving the tower. Basin heaters, tower draindown, and other freeze protection methods are often employed in cold climates.
  • Do not operate the tower unattended.
  • Do not operate the tower without a heat load. This can include basin heaters and heat trace. Basin heaters maintain the temperature of the water in the tower pan at an acceptable level. Heat trace is a resistive element that runs along water pipes located in cold climates to prevent freezing.
  • Maintain design water flow rate over the fill.
  • Manipulate airflow to maintain water temperature above freezing point.

Some commonly used terms in the cooling tower industry

  • Drift - Water droplets that are carried out of the cooling tower with the exhaust air. Drift droplets have the same concentration of impurities as the water entering the tower. The drift rate is typically reduced by employing baffle-like devices, called drift eliminators, through which the air must travel after leaving the fill and spray zones of the tower. Drift can also be reduced by using warmer entering cooling tower temperatures.
  • Blow-out - Water droplets blown out of the cooling tower by wind, generally at the air inlet openings. Water may also be lost, in the absence of wind, through splashing or misting. Devices such as wind screens, louvers, splash deflectors and water diverters are used to limit these losses.
  • Plume - The stream of saturated exhaust air leaving the cooling tower. The plume is visible when water vapor it contains condenses in contact with cooler ambient air, like the saturated air in one's breath fogs on a cold day. Under certain conditions, a cooling tower plume may present fogging or icing hazards to its surroundings. Note that the water evaporated in the cooling process is "pure" water, in contrast to the very small percentage of drift droplets or water blown out of the air inlets.
  • Blow-down - The portion of the circulating water flow that is removed in order to maintain the amount of dissolved solids
    Total dissolved solids
    Total Dissolved Solids is a measure of the combined content of all inorganic and organic substances contained in a liquid in: molecular, ionized or micro-granular suspended form. Generally the operational definition is that the solids must be small enough to survive filtration through a sieve...

     and other impurities at an acceptable level. It may be noted that higher TDS (total dissolved solids) concentration in solution results in greater potential cooling tower efficiency. However the higher the TDS concentration, the greater the risk of scale, biological growth and corrosion. The amount of blow-down is primarily designated by the electrical conductivity of the circulating water. Biological growth, scaling and corrosion can be prevented by chemicals (Biocid, Sulfric Acid, corrosion inhibitor). On the other hand, the only way to decrease the electrical conductivity is increasing the amount of blow-down and subsequently increasing the amount of make up.
  • Make up - The water that is needed to be added to the circulating water system in order to compensate water losses such as, evaporation, drift loss, blow-out, etc.
  • Leaching - The loss of wood preservative chemicals by the washing action of the water flowing through a wood structure cooling tower.
  • Noise - Sound energy emitted by a cooling tower and heard (recorded) at a given distance and direction. The sound is generated by the impact of falling water, by the movement of air by fans, the fan blades moving in the structure, and the motors, gearboxes or drive belts.
  • Approach - The approach is the difference in temperature between the cooled-water temperature and the entering-air wet bulb temperature
    Wet-bulb temperature
    The wet-bulb temperature is a type of temperature measurement that reflects the physical properties of a system with a mixture of a gas and a vapor, usually air and water vapor. Wet bulb temperature is the lowest temperature that can be reached by the evaporation of water only. It is the...

     (twb). Since the cooling towers are based on the principles of evaporative cooling, the maximum cooling tower efficiency depends on the wet bulb temperature of the air. The wet-bulb temperature is a type of temperature measurement that reflects the physical properties of a system with a mixture of a gas and a vapor, usually air and water vapor
  • Range - The range is the temperature difference between the water inlet and water exit.
  • Fill - Inside the tower, fills are added to increase contact surface as well as contact time between air and water. Thus they provide better heat transfer. The efficiency of the tower also depends on them. There are two types of fills that may be used:
    • Film type fill (causes water to spread into a thin film)
    • Splash type fill (breaks up water and interrupts its vertical progress)
  • Full-Flow Filtration- Full-flow filtration continuously strains the entire system flow. For example, in a 100-ton system, the flow rate would be roughly 300 gal/min. A filter would be selected to accommodate the entire 300 gal/min flow rate. In this case, the filter typically is installed after the cooling tower on the discharge side of the pump. While this is the preferred method of filtration, for higher flow systems, it may be cost prohibitive.
  • Side-Stream Filtration- Side-stream filtration, although popular, does not provide complete protection, but it can be effective. With side-stream filtration, a portion of the water is filtered continuously. This method works on the principle that continuous particle removal will keep the system clean. Manufacturers typically package side-stream filters on a skid, complete with a pump and controls. For high flow systems, this method is cost-effective.


Properly sizing a side-stream filtration system is critical to obtain satisfactory filter performance. There is some debate over how to properly size the side-stream system. Many engineers size the system to continuously filter the cooling tower basin water at a rate equivalent to 10% of the total circulation flow rate. For example, if the total flow of a system is 1,200 gal/min (a 400-ton system), a 120 gal/min side-stream system is specified.
  • Cycle of concentration - Maximum allowed multiplier for the amount of miscellaneous substances in circulating water by the amount of those substances in make-up water.
  • Treated timber - A structural material for cooling towers which was largely abandoned about 10 years ago. It is still used due to its low costs. The life of treated timber varies a lot, depending on the operating conditions of tower, such as frequency of stops, treatment of the circulating water, etc. Considering proper working conditions, estimated life of treated timber structural member is about 10 years.
  • Pultruded FRP - A common structure material for cooling towers, known for its high corrosion resistance capabilities. Pultuded FRP is produced using pultrusion
    Pultrusion
    Pultrusion is a continuous process for manufacture of composite materials with constant cross-section. Reinforced fibers are pulled through a resin, possibly followed by a separate preforming system, and into a heated die, where the resin undergoes polymerization...

     technology and became the most common structure material for cooling towers as it offers lower costs and requires less maintenance compared to reinforced concrete.

Fire hazards

Cooling towers which are constructed in whole or in part of combustible materials can support propagating internal fires. The resulting damage can be sufficiently severe to require the replacement of the entire cell or tower structure. For this reason, some code
Model building code
A model building code is a building code that is developed and maintained by a standards organization independent of the jurisdiction responsible for enacting the building code. A local government can choose to adopt a model building code as their own. This saves local governments the expense and...

s and standards recommend combustible cooling towers be provided with an automatic fire sprinkler system. Fires can propagate internally within the tower structure during maintenance when the cell is not in operation (such as for maintenance or construction), and even when the tower is in operation, especially those of the induced-draft type because of the existence of relatively dry areas within the towers.

Stability

Being very large structures, they are susceptible to wind damage, and several spectacular failures have occurred in the past. At Ferrybridge power station
Ferrybridge power station
The Ferrybridge power stations refers to a series of three coal-fired power stations situated on the River Aire in West Yorkshire, England. The first station on the site, Ferrybridge A power station, was constructed in the mid-1920s, and was closed as the second station, Ferrybridge B power...

 on 1 November 1965, the station was the site of a major structural failure
Structural failure
Structural failure refers to loss of the load-carrying capacity of a component or member within a structure or of the structure itself. Structural failure is initiated when the material is stressed to its strength limit, thus causing fracture or excessive deformations...

, when three of the cooling towers collapsed owing to vibrations in 85 mi/h winds. Although the structures had been built to withstand higher wind speeds, the shape of the cooling towers meant that westerly winds were funnelled into the towers themselves, creating a vortex
Vortex
A vortex is a spinning, often turbulent,flow of fluid. Any spiral motion with closed streamlines is vortex flow. The motion of the fluid swirling rapidly around a center is called a vortex...

. Three out of the original eight cooling towers were destroyed and the remaining five were severely damaged. The towers were rebuilt and all eight cooling towers were strengthened to tolerate adverse weather conditions. Building codes were changed to include improved structural support, and wind tunnel
Wind tunnel
A wind tunnel is a research tool used in aerodynamic research to study the effects of air moving past solid objects.-Theory of operation:Wind tunnels were first proposed as a means of studying vehicles in free flight...

 tests introduced to check tower structures and configuration.

European Market

The Cooling Tower market is composed of one third of "close wet" units and two thirds of "open wet" units, and reaches in 2010 a total of 190,24M€.

The market by country is splitted in 2010 as following:
Countries Sales Volume in M€ Share
Benelux 18.70 9.8%
France 22.48 11.8%
Germany 41.40 21.8%
Greece 1.82 1.0%
Italy 20.48 10.8%
Poland 6.31 3.3%
Portugal 2.72 1.4%
Russia, Ukraine and CIS countries 16.59 8.7%
Scandinavia 4.64 2.4%
Spain 9.47 5.0%
Switzerland 5.33 2.8%
Turkey 8.50 4.5%
UK and Ireland 13.66 7.2%
Eastern Europe 18.16 9.5%

See also

  • Architectural engineering
    Architectural engineering
    Architectural engineering, also known as building engineering, is the application of engineering principles and technology to building design and construction...

  • Cooling water
  • Deep lake water cooling
    Deep lake water cooling
    Deep lake water cooling uses cold water pumped from the bottom of a lake as a heat sink for climate control systems. Because heat pump efficiency improves as the heat sink gets colder, deep lake water cooling can reduce the electrical demands of large cooling systems where it is available...

  • Evaporative cooler
  • Fossil fuel power plant
    Fossil fuel power plant
    A fossil-fuel power station is a power station that burns fossil fuels such as coal, natural gas or petroleum to produce electricity. Central station fossil-fuel power plants are designed on a large scale for continuous operation...

  • HVAC
    HVAC
    HVAC refers to technology of indoor or automotive environmental comfort. HVAC system design is a major subdiscipline of mechanical engineering, based on the principles of thermodynamics, fluid mechanics, and heat transfer...

     (Heating, ventilating and air conditioning)
  • Hyperboloid structure
    Hyperboloid structure
    Hyperboloid structures are architectural structures designed with hyperboloid geometry. Often these are tall structures such as towers where the hyperboloid geometry's structural strength is used to support an object high off the ground, but hyperboloid geometry is also often used for decorative...

  • Mechanical engineering
    Mechanical engineering
    Mechanical engineering is a discipline of engineering that applies the principles of physics and materials science for analysis, design, manufacturing, and maintenance of mechanical systems. It is the branch of engineering that involves the production and usage of heat and mechanical power for the...

  • Power station
    Power station
    A power station is an industrial facility for the generation of electric energy....