Knob and tube wiring
Encyclopedia
Knob and tube wiring was an early standardized method of electrical wiring
Electrical wiring
Electrical wiring in general refers to insulated conductors used to carry electricity, and associated devices. This article describes general aspects of electrical wiring as used to provide power in buildings and structures, commonly referred to as building wiring. This article is intended to...

 in buildings, in common use in North America from about 1880 to the 1930s. It consisted of single-insulated copper
Copper
Copper is a chemical element with the symbol Cu and atomic number 29. It is a ductile metal with very high thermal and electrical conductivity. Pure copper is soft and malleable; an exposed surface has a reddish-orange tarnish...

 conductors
Electrical conductor
In physics and electrical engineering, a conductor is a material which contains movable electric charges. In metallic conductors such as copper or aluminum, the movable charged particles are electrons...

 run within wall or ceiling cavities, passing through joist
Joist
A joist, in architecture and engineering, is one of the horizontal supporting members that run from wall to wall, wall to beam, or beam to beam to support a ceiling, roof, or floor. It may be made of wood, steel, or concrete. Typically, a beam is bigger than, and is thus distinguished from, a joist...

 and stud
Wall stud
A wall stud is a vertical member in the light frame construction techniques called balloon framing and platform framing of a building's wall.-Purpose:...

 drill-holes via protective porcelain insulating tubes, and supported along their length on nailed-down porcelain knob insulators. Where conductors entered a wiring device such as a lamp or switch, or were pulled into a wall, they were protected by flexible cloth insulating
Electrical insulation
thumb|250px|[[Coaxial Cable]] with dielectric insulator supporting a central coreThis article refers to electrical insulation. For insulation of heat, see Thermal insulation...

 sleeving called loom. The first insulation was asphalt-saturated cotton cloth, then rubber became common. Wire splices in such installations were twisted together for good mechanical strength, then solder
Solder
Solder is a fusible metal alloy used to join together metal workpieces and having a melting point below that of the workpiece.Soft solder is what is most often thought of when solder or soldering are mentioned and it typically has a melting range of . It is commonly used in electronics and...

ed and wrapped with rubber insulating tape and friction tape
Friction tape
Friction tape is a type of adhesive tape made from cloth impregnated with a rubber-based adhesive and is mainly used to increase grip or friction. Because the adhesive is impregnated in the cloth, friction tape is sticky on both sides. The rubber based adhesive makes it an electrical insulator and...

 (asphalt saturated cloth), or made inside metal junction boxes.

Knob and tube wiring was eventually displaced from interior wiring systems because of the high cost of installation compared with use of power cables, which combined both power conductors of a circuit in one run (and which later included grounding conductors).

At present, new knob and tube installations are permitted in the US only in a few very specific situations listed in the National Electrical Code, such as certain industrial and agricultural environments.

Elements

Ceramic
Ceramic
A ceramic is an inorganic, nonmetallic solid prepared by the action of heat and subsequent cooling. Ceramic materials may have a crystalline or partly crystalline structure, or may be amorphous...

 knobs were cylindrical and generally nailed directly into the wall studs or floor joists. Most had a circular groove running around their circumference, although some were constructed in two pieces with pass-through grooves on each side of the nail in the middle. A leather washer often cushioned the ceramic, to reduce breakage during installation.

By wrapping electrical wires around the knob, and securing them with tie wires, the knob securely and permanently anchored the wire. The knobs separated the wire from potentially combustible framework, facilitated changes in direction, and ensured that wires were not subject to excessive tension. Because the wires were suspended in air, they could dissipate heat well.

Ceramic tubes were inserted into holes bored in wall studs or floor joists, and the wires were directed through them. This kept the wires from coming into contact with the wood framing members and from being compressed by the wood as the house settled. Ceramic tubes were sometimes also used when wires crossed over each other, for protection in case the upper wire were to break and fall on the lower conductor.

Ceramic cleats, which were block-shaped pieces, served a purpose similar to that of the knobs.

Ceramic bushings protected each wire entering a metal device box, when such an enclosure was used.

Loom, a woven flexible insulating sleeve, was slipped over insulated wire to provide additional protection whenever a wire passed over or under another wire, when a wire entered a metal device enclosure, and in other situations prescribed by code.

Other ceramic pieces would typically be used as a junction point between the wiring system proper, and the more flexible cloth-clad wiring found in light fixtures or other permanent, hard-wired devices. When a generic power outlet was desired, the wiring could run directly into the junction box
Junction box
An electrical junction box is a container for electrical connections, usually intended to conceal them from sight and meter tampering. A small metal or plastic junction box may form part of an electrical conduit wiring system in a building, or may be buried in the plaster of a wall, concealed...

 through a tube of protective loom and a ceramic bushing.

Wiring devices such as light switches, receptacle outlets, and lamp sockets were either surface-mounted, suspended, or flush-mounted within walls and ceilings. Only in the last case were metal boxes always used to enclose the wiring and device.

Unusual wiring layouts

In many older K&T installations, the supply and return wires were routed separately from each other, rather than being located parallel to and near each other. This direct routing method has the advantage of reduced cost by allowing use of the shortest possible lengths of wire, but the major disadvantage that a detailed building wiring diagram is needed for other electricians to understand multiple interwoven circuits, especially if the wiring is not fully visible throughout its length. By contrast, modern electrical codes now require that all residential wiring connections be made only inside protective enclosures, such as junction boxes, and that all connections must remain accessible for inspection, troubleshooting, repair, or modification.

For example, consider the installation of a light, controlled by two switches in different locations. In modern practice, the supply and return wires both arrive at the first switch, where the supply is connected to one of the two switching wires (hot/red); the return wire is carried inside the same multi-conductor cable to the distant switch second switch. From there, a supply wire carries power to the light, and a return wire goes back to location of the second switch, and then retraces the path back to the fusebox.

For older K&T installations, the supply and return wires were not necessarily installed as a pair, and did not necessarily have to be near each other at all. From the fusebox, a single supply wire would go to the first switch. From there, it would divide into two switching wires. At the second, remote switch the two wires would come together to be a single supply wire again. Finally this supply wire would be routed from the second switch to the light fixture, and then a single return wire would take the shortest path through the building back to the fusebox. The foregoing is an example of the so-called Carter system wire layout, which is described in more detail in a separate article.

In the case of modern North American split phase power, the supply wires from two opposite single-phase circuit breakers are used to supply 240VAC for high power devices. In modern circuits, these two wires are grouped together, and for each 240V device a dedicated circuit is installed, usually with the two circuit breakers ganged together to operate simultaneously.

But with old K&T, a past electrician might have reasoned as follows: "I have a 20 amp circuit on one phase over here, and another 20 amp circuit on an opposite phase over there. Rather than run an entirely new set of wires for this one device, I will just tap off the supply wires of those two circuits and bring them together for this one device." This method of wiring does work and it reduces the amount of wire used, but it makes electrical problems very hard to find and fix, with (possibly undocumented) wires going all over the place within the walls and ceilings, to whatever was the most expedient supply or return wire at the time of installation.

Under the US electrical code, Carter system wiring layouts have now been banned, even for permissible new installations of K&T wiring. However, electricians must be aware of this older system, which may still be present in existing electrical installations.

Neutral fusing

Another practice that was common (and even required) in some older K&T designs was the installation of separate fuses in both the hot wire and the neutral
Ground and neutral
Since the neutral point of an electrical supply system is often connected to earth ground, ground and neutral are closely related. Under certain conditions, a conductor used to connect to a system neutral is also used for grounding of equipment and structures...

 (return) wire of an electrical circuit. The failure of a neutral fuse would cut off power flow through the affected circuit, but the hot conductor could still remain hot relative to ground
Earthing system
In electricity supply systems, an earthing system defines the electrical potential of the conductors relative to the Earth's conductive surface. The choice of earthing system can affect the safety and electromagnetic compatibility of the power supply, and regulations can vary considerably among...

, an unexpected and potentially hazardous situation. Because of the presence of a neutral fuse, the neutral conductor could not be relied on to remain near ground potential, and could in fact be at full line potential instead (via transmission of voltage through a switched-on light bulb, for example).

Modern electrical codes do not require a neutral fuse, and instead explicitly forbid such configurations that might break continuity of the neutral conductor.

Advantages

When originally installed in the early 1900s, K&T wiring was less expensive than other wiring methods. For several decades, electricians could choose between using K&T wiring on one hand, compared to conduit, armored cable, and metal junction boxes on the other. The conduit methods were known to be of better quality, but their cost was significantly higher than that of K&T. In 1909, flexible armored cable cost about twice the cost of K&T, and conduit cost about three times the cost for K&T. Knob and tube wiring persisted since it allowed owners to wire a building for electricity at lower cost.

Modern wiring methods assume two or more load-carrying conductors will lie very near each other, as for instance in standard NM-2 cable. Since the load-carrying wires are in close proximity, when they heat up, the heating is shared across the wires, limiting the overall current load they can support. Since the load-carrying wires in K&T wiring are widely spaced, the wires are capable of carrying higher loads without risk of fire, making it a safe wiring method. It is actually, when used correctly, safer than most modern wiring methods, since the wires are held away from the structural materials by ceramic insulators.

K&T wiring was commonly insulated with cotton cloth and soft rubber, in addition to the porcelain standoffs. Although the actual wire covering may have degraded over the decades, the porcelain standoffs have a nearly unlimited lifespan and will keep any bare wires safely insulated. Today, porcelain standoffs are still commonly used with bare wire electric fencing for livestock, and such porcelain standoffs carry far higher voltage surges without risk of shorting to ground.

In short, K&T wiring which was installed correctly, and not damaged or incorrectly modified since then, is extremely safe when used within the original current-carrying limits.

Disadvantages

Historically, wiring installation requirements were less demanding in the age of knob-and-tube wiring than today. Compared to modern electrical wiring standards, these are the main technical shortcomings of knob-and-tube wiring methods:
  • never included a safety grounding conductor
  • did not confine switching to the hot conductor (the so-called Carter system places electrical loads across the common terminals of a three-way switch pair)
  • permitted the use of in-line splices in walls without a junction box (thus exposing the potential fire hazard of an uncontained spark caused by arcing following mechanical failure of the splice).


Over time, the price of electrician labor grew faster than the cost of materials. This removed the price advantage of K&T methods, especially since they required time-consuming skillful soldering of in-line splices and junctions, and careful hand-wrapping of connections in layers of insulating tape.

Knob-and-tube wiring can be made with high current carrying capacity. However, most existing residential knob and tube installations, dating to before 1940, have fewer branch circuits than is desired today. While these installations were adequate for the electrical loads at the time of installation, modern households use a range and intensity of electrical equipment unforeseen at the time. Household power use increased dramatically following World War II due to wide availability of electrical appliances.

Modern home buyers often find that existing K&T systems lack the capacity for today's levels of power use. First-generation wiring systems became susceptible to abuse by homeowners who would replace blown fuses
Fuse (electrical)
In electronics and electrical engineering, a fuse is a type of low resistance resistor that acts as a sacrificial device to provide overcurrent protection, of either the load or source circuit...

 with fuses rated for higher current. This overfusing of the circuits subjects wiring to higher levels of current and risks heat damage.

Knob-and-tube wiring may also be damaged by building renovations. Its cloth and rubber insulation can dry out and turn brittle. It may also be damaged by rodents and careless activities such as hanging objects from wiring running in accessible areas like basement
Basement
__FORCETOC__A basement is one or more floors of a building that are either completely or partially below the ground floor. Basements are typically used as a utility space for a building where such items as the furnace, water heater, breaker panel or fuse box, car park, and air-conditioning system...

s.

For those concerned about stray magnetic field
Magnetic field
A magnetic field is a mathematical description of the magnetic influence of electric currents and magnetic materials. The magnetic field at any given point is specified by both a direction and a magnitude ; as such it is a vector field.Technically, a magnetic field is a pseudo vector;...

s, K&T wiring produces a much stronger effect at a given level of current, since the conductors are separated by a greater distance and their fields do not cancel as well as more closely spaced conductors. According to the theory of magnetic fields, two parallel conductors carrying equal currents in opposite directions form a balanced line
Balanced line
In telecommunications and professional audio, a balanced line or balanced signal pair is a transmission line consisting of two conductors of the same type, each of which have equal impedances along their lengths and equal impedances to ground and to other circuits. The chief advantage of the...

, partially cancelling each other's magnetic field at a sufficiently large distance from the pair. As a rule of thumb, if two parallel conductors carrying opposite currents are then separated by 10 times the distance, the stray magnetic field will then extend 10 times further than before.

Currently, the United States National Electrical Code
National Electrical Code (US)
The National Electrical Code , or NFPA 70, is a regionally adoptable standard for the safe installation of electrical wiring and equipment...

 forbids the use of loose, blown-in, or expanding foam insulation
Building insulation
building insulation refers broadly to any object in a building used as insulation for any purpose. While the majority of insulation in buildings is for thermal purposes, the term also applies to acoustic insulation, fire insulation, and impact insulation...

 over K&T wiring. This is because K&T is designed to let heat dissipate to the surrounding air. As a result, energy efficiency upgrades that involve insulating previously uninsulated walls usually also require replacement of the wiring in affected homes. However, California and Washington, as well as possibly other states, have actually reversed the ruling on insulation around K&T. They did not find a single fire that was attributed to K&T, and permit insulation provided the home first passes inspection by an electrician.

As existing K&T wiring gets older, insurance companies may deny coverage due to a perception of increased risk. Several companies will not write new homeowners policies
Home insurance
Home insurance, also commonly called hazard insurance or homeowner's insurance , is the type of property insurance that covers private homes...

at all unless all K&T wiring is replaced, or an electrician certifies that the wiring is in good condition. Also, many institutional lenders are unwilling to finance a home with limited ampacity (current carrying capacity) service (which, as noted above, often goes hand-in-hand with K&T wiring), unless the electrical service is upgraded.