Ufer Ground
Encyclopedia
The Ufer Ground is an electrical earth grounding
Ground (electricity)
In electrical engineering, ground or earth may be the reference point in an electrical circuit from which other voltages are measured, or a common return path for electric current, or a direct physical connection to the Earth....

 method developed during World War II. It uses a concrete-encased electrode to improve grounding in dry areas. The technique is used in construction of concrete foundations.

History

During World War II, the U.S. Army required a grounding system for bomb storage vaults near Tucson and Flagstaff, Arizona. Conventional grounding systems did not work well in this location since the desert terrain had no water table and very little rainfall. The extremely dry soil conditions would have required hundreds of feet of copper rods to be inserted into the ground in order to create a low enough impedance ground to protect the buildings from lightning strikes.

In 1942, Herbert G. Ufer was a consultant working for the U.S. Army. Ufer was given the task of finding a lower cost and more practical alternative to traditional copper rod grounds for these dry locations. Ufer discovered that concrete had better conductivity than most types of soil. Ufer then developed a grounding scheme based around encasing the grounding conductors in concrete. This method proved to be very effective, and was implemented throughout the Arizona test site.

After the war, Ufer continued to test his grounding method, and his results were published in a paper presented at the IEEE Western Appliance Technical Conference in 1963. The use of concrete enclosed grounding conductors was added to the U.S. National Electrical Code (NEC) in 1968. It was not required to be used if a water pipe or other grounding electrode was present. In 1978, the NEC required rebar to be used as a grounding electrode if present. The NEC refers to this type of ground as a "Concrete Encased Electrode" (CEE) instead of using the name Ufer ground.

Over the years, the term "Ufer Ground" has become synonymous with the use of any type of concrete enclosed grounding conductor, whether it conforms to Ufer's original grounding scheme or not.

Construction

Ufer discovered that the naturally high pH level in concrete meant that it had a ready supply of ions, and would provide a better electrical ground than almost any type of soil. Ufer also found that the soil around the concrete became "doped", and its subsequent rise in pH caused the overall impedance of the soil itself to be reduced. The concrete enclosure also increases the surface area of the connection between the grounding conductor and the surrounding soil, which also helps to reduce the overall impedance of the connection.

Ufer's original grounding scheme used copper encased in concrete. However, the high pH of concrete often causes the copper to chip and flake. For this reason, steel is often used instead of copper.

When homes are built on concrete slabs, it is common practice to bring one end of the rebar
Rebar
A rebar , also known as reinforcing steel, reinforcement steel, rerod, or a deformed bar, is a common steel bar, and is commonly used as a tensioning device in reinforced concrete and reinforced masonry structures holding the concrete in compression...

up out of the concrete at a convenient location to make an easy connection point for the grounding electrode.

Ufer grounds, when present, are preferred over the use of grounding rods. In some areas (like Des Moines, Iowa) Ufer grounds are required for all residential and commercial buildings. The conductivity of the soil usually determines if Ufer grounds are required in any particular area.

An Ufer ground of specified minimum dimensions is recognized by the U.S. National Electrical Code as a grounding electrode. The grounding conductors must have sufficient cover by the concrete to prevent damage when dissipating high-current lightning strikes.

A disadvantage of Ufer grounds is that the moisture in the concrete can flash into steam during a lightning strike or similar high energy fault condition. This can crack the surrounding concrete and damage the building foundation.

External links

The source of this article is wikipedia, the free encyclopedia.  The text of this article is licensed under the GFDL.
 